Adler Merano 180 stop when circulatore start

« Older   Newer »
 
  Share  
.
  1. olivier_be
     
    .

    User deleted


    Hello,

    I got a problem with the board of my adler 180.

    It was replaced under warranty and now the problem I had is solved (fume was always at 30°)

    But now, the stufa is stopping (eco) when circulator is starting. Like if max temperature of the stuf and circulator start temperature are similar. So the stuf is always stopping when at 65° and then stop and then start again and so on.

    Only the 2 nearest radiatore are warm, others are cold

    When dubbel clic on set I have 65° for H20

    I take a look at UT04 parameters without changing anything and here's what I have :

    PR12 : 30
    PR13 : 40
    PR14 : 210
    PR15 : 65
    PR27 : 65

    Also the air of the ventilator in front of the stove is cold :-(

    Should I / Could I change someting in the PR parameters or does anyone have an idea ?

    Thanks, best regards
     
    Top
    .
  2.  
    .
    Avatar

    SUPERNOVA

    Group
    Member
    Posts
    14,211
    Location
    Montagna Pistoiese

    Status
    Anonymous
    Clicca
     
    Top
    .
  3. olivier_be
     
    .

    User deleted


    Thanks for the answer but I allready check on the forum before asking and I found othing similar to my problem and/or my PR menu

    Best regards
     
    Top
    .
  4. olivier_be
     
    .

    User deleted


    For information : the new board was programmed for a 12 Kw. I got technical service on the phone et they help me to put the correct configuration
     
    Top
    .