    Hello to everyone.I apologize for having to write in English, but I couldn't find another forum.maybe someone could help.
    I bought a house wich has an Edilkamin Blade h 22 ,and I wonder if its there any chance I could set up the water pump to transfer the water faster?
    Im asking that because i believe the pump does not cope with the whole system(I could be wrong).how can I ventilate the entire system outside using the classic method with radiators?
    any help is appreciated.thank you .
    185qm
    14 radiators
    2 floors.
     
    Top
    .
  2.  
    .
    Avatar

    SUPERNOVA

    Group
    Member
    Posts
    14,210
    Location
    Montagna Pistoiese

    Status
    Anonymous
    CITAZIONE (Petru Laurentiu Lupu @ 24/2/2024, 00:06) 
    Hello to everyone.I apologize for having to write in English, but I couldn't find another forum.maybe someone could help.
    I bought a house wich has an Edilkamin Blade h 22 ,and I wonder if its there any chance I could set up the water pump to transfer the water faster?
    Im asking that because i believe the pump does not cope with the whole system(I could be wrong).how can I ventilate the entire system outside using the classic method with radiators?
    any help is appreciated.thank you .
    185qm
    14 radiators
    2 floors.
    *************************
    Ciao a tutti.Mi scuso se devo scrivere in inglese, ma non sono riuscito a trovare un altro forum.forse qualcuno potrebbe aiutarmi.
    Ho comprato una casa che ha una Edilkamin Blade h 22, e mi chiedo se c'è qualche possibilità di poter installare la pompa dell'acqua per trasferire l'acqua più velocemente?
    Lo chiedo perché credo che la pompa non sia in grado di gestire l'intero sistema (potrei sbagliarmi). Come posso ventilare l'intero sistema all'esterno utilizzando il metodo classico con i radiatori?
    Ogni aiuto è apprezzato, grazie .
    185 mq
    14 radiatori
    2 piani.

    Hi Lupu!!
    Leggi la discussione che ti linko.
    https://stufapellet.forumcommunity.net/?t=59588444
     
    Top
    .
  3.  
    .
    Avatar

    infreddolito perso

    Group
    Member
    Posts
    11

    Status
    Offline
    Hi,I read that topic before ,but my Blade h 22 Its from 2020 and the pump its different and I couldn't find something that will help me and also the google translate doesnt help me 100%...
    I was looking for some parameters for the pump but I ve seen în tehnic menu that my pump its set to 100,but I dont know exactly whats that means ,100% or ?
    Attached Image
    Screenshot_20240224_112853_Chrome

     
    Top
    .
  4.  
    .
    Avatar

    SUPERNOVA

    Group
    Member
    Posts
    14,210
    Location
    Montagna Pistoiese

    Status
    Anonymous
    CITAZIONE (Petru Laurentiu Lupu @ 24/2/2024, 11:32) 
    Hi,I read that topic before ,but my Blade h 22 Its from 2020 and the pump its different and I couldn't find something that will help me and also the google translate doesnt help me 100%...
    I was looking for some parameters for the pump but I ve seen în tehnic menu that my pump its set to 100,but I dont know exactly whats that means ,100% or ?
    *****************
    Ciao, ho già letto quell'argomento, ma il mio Blade h 22 è del 2020 e la pompa è diversa e non sono riuscito a trovare qualcosa che mi possa aiutare e anche Google Translate non mi aiuta al 100%...
    Stavo cercando alcuni parametri per la pompa ma ho visto nel menu tecnico che la mia pompa è impostata su 100, ma non so esattamente cosa significhi: 100% o?

    Mi spiace ma io non lo so, aspetta l'intervento di qualcuno esperto di idraulica.
     
    Top
    .
  5.  
    .
    Avatar

    infreddolito perso

    Group
    Member
    Posts
    11

    Status
    Offline
    Do you have maybe the parameters from blade h 22 only to check if mine s are okay ? Thank you for your time.
     
    Top
    .
  6.  
    .
    Avatar

    SUPERNOVA

    Group
    Member
    Posts
    14,210
    Location
    Montagna Pistoiese

    Status
    Anonymous
    CITAZIONE (Petru Laurentiu Lupu @ 24/2/2024, 20:08) 
    Do you have maybe the parameters from blade h 22 only to check if mine s are okay ? Thank you for your time.
    ***************
    Hai magari i parametri del blade h 22 solo per verificare se i miei vanno bene? Grazie per il tuo tempo.

    Quando si entra nell'area tecnica ci sono le impostazioni da definire in sede di installazione da parte del CAT (che ovviamente non ho).
    Una di queste è poi la lista dei parametri veri e propri che è inopportuno modificare.
    Tu di dove sei, della Romania?
     
    Top
    .
  7.  
    .
    Avatar

    infreddolito perso

    Group
    Member
    Posts
    11

    Status
    Offline
    I have made small changes already, after what I saw on the forum. related to the flame, pellets ...
    From Romania but I live in Germany so my nearest CAT its far from me and they dont wanna come and check it ...thats why I am asking here ...
     
    Top
    .
  8.  
    .
    Avatar

    SUPERNOVA

    Group
    Gli allegri incendiari
    Posts
    11,854
    Location
    FVG

    Status
    Online
    HI
    14 radiators
    are many.
    do you have collectors between the stove and radiators?
    pipe diameter between stove and collectors?

    ciao
    14 radiatori
    sono molti.
    hai collettori tra stufa e radiatori?
    diametro tubi tra stufa e collettori?
     
    Top
    .
  9.  
    .
    Avatar

    SUPERNOVA

    Group
    Member
    Posts
    14,210
    Location
    Montagna Pistoiese

    Status
    Anonymous
    CITAZIONE (Petru Laurentiu Lupu @ 24/2/2024, 20:46) 
    I have made small changes already, after what I saw on the forum. related to the flame, pellets ...
    From Romania but I live in Germany so my nearest CAT its far from me and they dont wanna come and check it ...thats why I am asking here ...
    ********************
    Ho già apportato piccole modifiche, dopo quello che ho visto sul forum. legati alla fiamma, al pellet...
    Dalla Romania ma vivo in Germania quindi il mio CAT più vicino è lontano da me e non vogliono venire a controllarlo... ecco perché lo chiedo qui...

    Le modifiche che hai apportato le hai fatte dal menù CAMINO e RICETTA PLT ??
    Ho visto che è intervenuto un ottimo tecnico idraulico a darti una mano, fai quello che ti dice.
    Per i parametri e le relative impostazioni ti consiglio di rivolgerti via mail ad un bravo CAT che sta in Romania ... tra connazionali dovreste intendervi.
    https://stufapellet.forumcommunity.net/?ac...le&MID=11468651
     
    Top
    .
  10.  
    .
    Avatar

    infreddolito perso

    Group
    Member
    Posts
    11

    Status
    Offline
    actually 13 radiators (one its closed) 15" cooper pipe .what do you mean by "manifolds between the stove ?"
     
    Top
    .
  11.  
    .
    Avatar

    SUPERNOVA

    Group
    Gli allegri incendiari
    Posts
    11,854
    Location
    FVG

    Status
    Online
    This
    Attached Image
    Screenshot_20240224_210430_Google

     
    Top
    .
  12.  
    .
    Avatar

    infreddolito perso

    Group
    Member
    Posts
    11

    Status
    Offline
    Yes,this is located on the basement
    Attached Image
    Screenshot_20240224_210647_Messenger

     
    Top
    .
  13.  
    .
    Avatar

    SUPERNOVA

    Group
    Gli allegri incendiari
    Posts
    11,854
    Location
    FVG

    Status
    Online
    Ci sono errori di installazione degli sfiati.

    Lo hai fatto tu?

    Ci sono errori di installazione degli sfiati.

    Lo hai fatto tu?

    Tubi in rame?
    Diametro delle colonne?
     
    Top
    .
  14.  
    .
    Avatar

    infreddolito perso

    Group
    Member
    Posts
    11

    Status
    Offline
    I think its not well ventilated.all the pipe are from cooper.
    The house I buy it the way its looks in the picture.
    The main distribution its from 18" diameter ,the radiators have 15"diameter ,closed circuit
    Attached Image
    Screenshot_20240224_211246_Messenger

     
    Top
    .
  15.  
    .
    Avatar

    SUPERNOVA

    Group
    Gli allegri incendiari
    Posts
    11,854
    Location
    FVG

    Status
    Online
    Rame 18mm è troppo piccolo per 14 radiatori.
    18mm è considerato 3/4".

    Non è adatto al flusso di 14 radiatori.
    La stufa non ha problemi a scaldare il puffer.

    Hai 1 o 2 circolatore secondario?
     
    Top
    .